HVAC DTC Troubleshooting: 10
DTC indicator 10: A Problem in the Blower Motor Circuit
|
1. |
Problem verification:
Problem verification
|
?1. |
Turn the ignition switch to LOCK (0) and then back to ON (II). |
|
Is DTC 10 indicated?
|
|
|
|
|
|
|
Intermittent failure. Check for loose wires or poor connections on the blower motor circuit.? |
|
2. |
Fuse check:
Fuse check
|
?1. |
Turn the ignition switch to LOCK (0). |
|
?2. |
Check the following fuse.
|
Fuse |
No. A14 (40 A) |
|
Location |
Under-hood fuse/relay box | |
| | |
Is the fuse OK?
|
|
|
|
|
|
|
Replace the fuse, and recheck. If fuse blows again, repair a short in the No. A14 (40 A) fuse circuit.? |
|
3. |
Blower motor power circuit check:
Blower motor power circuit check
|
?1. |
Disconnect the following connector.
|
|
?2. |
Turn the ignition switch to LOCK (0). |
|
?3. |
Measure the voltage between test points 1 and 2.
|
Test condition |
IG ON (II) |
|
Blower motor 2P connector: disconnected |
|
Test circuit |
BLW-RLY |
|
Test point 1 |
Blower motor 2P connector No. 2 (WHT) |
|
Test point 2 |
Body ground | |
| | |
Is there battery voltage?
|
4. |
Blower motor operation check:
Blower motor operation check
|
?1. |
Turn the ignition switch to LOCK (0). |
|
?3. |
Connect terminals A and B with a jumper wire.
|
Terminal A |
Blower motor 2P connector No. 1 (GRN) |
|
Terminal B |
Body ground | |
|
|
|
?4. |
Turn the ignition switch ON (II). | |
Does the blower motor run at high speed?
|
5. |
Open wire check (GND line):
Open wire check (GND line)
|
?1. |
Turn the ignition switch to LOCK (0).. |
|
?2. |
Disconnect the jumper wire. |
|
?3. |
Disconnect the following connector.
|
|
?4. |
Check for continuity between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
Power transistor 4P connector: disconnected |
|
Test circuit |
GND |
|
Test point 1 |
Power transistor 4P connector No. 3 (BLK) |
|
Test point 2 |
Body ground | |
| | |
Is there continuity?
|
|
|
The GND wire is OK. Go to step 6. |
|
|
|
Check for an open in the wire between the power transistor and body ground. If the wire is OK, check for poor ground at G401.? |
|
6. |
Open wire check (BLW-M line):
Open wire check (BLW-M line)
|
?1. |
Connect terminals A and B with a jumper wire.
|
Terminal A |
Power transistor 4P connector No. 3 (BLK) |
|
Terminal B |
Power transistor 4P connector No. 4 (GRN) | |
|
|
|
?2. |
Turn the ignition switch ON (II). | |
Does the blower motor run at high speed?
|
|
|
The BLW-M wire is OK. Go to step 7. |
|
|
|
Repair an open in the wire between the power transistor and the blower motor.? |
|
7. |
Shorted wire check (BLOWER V/BLW-V line):
Shorted wire check (BLOWER V/BLW-V line)
|
?1. |
Turn the ignition switch to LOCK (0). |
|
?2. |
Disconnect the jumper wire. |
|
?3. |
Disconnect the following connector.
|
|
?4. |
Check for continuity between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
HVAC control unit 32P connector: disconnected |
|
Power transistor 4P connector: disconnected |
|
Test circuit |
BLOWER V/BLW-V |
|
Test point 1 |
HVAC control unit 32P connector No. 24 (BLU) |
|
Test point 2 |
Body ground | |
| | |
Is there continuity?
|
|
|
Repair a short to body ground in the wire between the HVAC control unit and the power transistor.? |
|
|
|
The BLOWER V/BLW-V wire is not shorted. Go to step 8. |
|
8. |
Shorted wire check (BLOWER G/BLW-G line):
Shorted wire check (BLOWER G/BLW-G line)
|
?1. |
Check for continuity between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
HVAC control unit 32P connector: disconnected |
|
Power transistor 4P connector: disconnected |
|
Test circuit |
BLOWER G/BLW-G |
|
Test point 1 |
HVAC control unit 32P connector No. 22 (YEL) |
|
Test point 2 |
Body ground | |
| | |
Is there continuity?
|
|
|
Repair a short to body ground in the wire between the HVAC control unit and the power transistor.? |
|
|
|
The BLOWER G/BLW-G wire is not shorted. Go to step 9. |
|
9. |
Open wire check (BLOWER G/BLW-G line):
Open wire check (BLOWER G/BLW-G line)
|
?1. |
Check for continuity between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
HVAC control unit 32P connector: disconnected |
|
Power transistor 4P connector: disconnected |
|
Test circuit |
BLOWER G/BLW-G |
|
Test point 1 |
HVAC control unit 32P connector No. 22 (YEL) |
|
Test point 2 |
Power transistor 4P connector No. 1 (YEL) | |
|
| |
Is there continuity?
|
|
|
The BLOWER G/BLW-G wire is OK. Go to step 10. |
|
|
|
Repair an open in the wire between the HVAC control unit and the power transistor.? |
|
10. |
Open wire check (BLOWER V/BLW-V line):
Open wire check (BLOWER V/BLW-V line)
|
?1. |
Check for continuity between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
HVAC control unit 32P connector: disconnected |
|
Power transistor 4P connector: disconnected |
|
Test circuit |
BLOWER V/BLW-V |
|
Test point 1 |
HVAC control unit 32P connector No. 24 (BLU) |
|
Test point 2 |
Power transistor 4P connector No. 2 (BLU) | |
|
| |
Is there continuity?
|
|
|
The BLOWER V/BLW-V wire is OK. Go to step 11. |
|
|
|
Repair an open in the wire between the HVAC control unit and the power transistor.? |
|
11. |
Power transistor check:
Power transistor check
|
Is the power transistor OK?
|
12. |
Blower motor relay check:
Blower motor relay check
|
?1. |
Turn the ignition switch to LOCK (0). |
|
?2. |
Remove the blower motor relay from the under-hood fuse/relay box, and test it. | |
Is the relay OK?
|
|
|
|
|
|
|
Replace the blower motor relay.? |
|
13. |
Open wire check (+B HTR MTR line):
Open wire check (+B HTR MTR line)
|
?1. |
Measure the voltage between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
Blower motor 2P connector: disconnected |
|
Blower motor relay: disconnected |
|
Test circuit |
+B HTR MTR |
|
Test point 1 |
Blower motor relay 4P socket No. 1 |
|
Test point 2 |
Body ground | |
| | |
Is there battery voltage?
|
|
|
The +B HTR MTR wire is OK. Go to step 14. |
|
|
|
|
|
14. |
Open wire check (IG2 A/C line):
Open wire check (IG2 A/C line)
|
?1. |
Turn the ignition switch ON (II). |
|
?2. |
Measure the voltage between test points 1 and 2.
|
Test condition |
IG ON (II) |
|
Blower motor 2P connector: disconnected |
|
Blower motor relay: disconnected |
|
Test circuit |
IG2 A/C |
|
Test point 1 |
Blower motor relay 4P socket No. 3 (LT GRN) |
|
Test point 2 |
Body ground | |
| | |
Is there battery voltage?
|
|
|
The IG2 A/C wire is OK. Go to step 15. |
|
|
|
Repair an open in the wire between the relay circuit board and the blower motor relay in the under-hood fuse/relay box, or between the No. B1 (7.5 A) fuse in the under-dash fuse/relay box and the relay circuit board in the under-hood fuse/relay box. If wires are OK, replace the relay circuit board.? |
|
15. |
Open wire check (GND line):
Open wire check (GND line)
|
?1. |
Turn the ignition switch to LOCK (0). |
|
?2. |
Check for continuity between test points 1 and 2.
|
Test condition |
IG LOCK (0) |
|
Blower motor 2P connector: disconnected |
|
Blower motor relay: disconnected |
|
Test circuit |
GND |
|
Test point 1 |
Blower motor relay 4P socket No. 4 (BLK) |
|
Test point 2 |
Body ground | |
| | |
Is there continuity?
|
|
|
Repair an open in the wire between the blower motor relay and the blower motor.? |
|
|
|
Check for an open in the wire between the blower motor relay and body ground. If the wire is OK, check for poor ground at G301.? | |